> On Jun 13, 2018, at 8:15 PM, Jim Brown <jim at audiosystemsgroup.com> wrote:
>
>> On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:
>> Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in the future a P3 Panadaper?
>
> Yes.
>
>> 2) If not can I get away with replacing the breaker with a 20A breaker?
>
> Only if all the wiring on that breaker is #12 or larger.
>
>> 30A?
>
> Only if all the wiring on that breaker is #10. These are electrical safety code requirements, which carry the force of law.
>
>> 3) Will the Alinco be big enough
>
> Yes
>
>> or should I upgrade that as well?
>
> No.
>
> 73, Jim K9YC
>
>