On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:
> Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in the future a P3 Panadaper?
Yes.
> 2) If not can I get away with replacing the breaker with a 20A breaker?
Only if all the wiring on that breaker is #12 or larger.
> 30A?
Only if all the wiring on that breaker is #10. These are electrical
safety code requirements, which carry the force of law.
> 3) Will the Alinco be big enough
Yes
> or should I upgrade that as well?
No.
73, Jim K9YC