[Elecraft] power requirements for a K3S, KPA500, KAT500, P3?
Charlie T
pincon at erols.com
Wed Jun 13 23:35:14 EDT 2018
AND, if there's any sort of electrical fire and it is discovered a 20 A breaker was installed with 14Ga wire, you fire insurance becomes instantly "non-functus".
That's Latin for "You're screwed".
Charlie k3ICH
-----Original Message-----
From: elecraft-bounces at mailman.qth.net <elecraft-bounces at mailman.qth.net> On Behalf Of Jim Brown
Sent: Wednesday, June 13, 2018 11:16 PM
To: elecraft at mailman.qth.net
Subject: Re: [Elecraft] power requirements for a K3S, KPA500, KAT500, P3?
On 6/13/2018 8:02 PM, Michael Gillen via Elecraft wrote:
> Will 15A house line supply enough juice for the K3S, KPA500, KAT500, and in the future a P3 Panadaper?
Yes.
> 2) If not can I get away with replacing the breaker with a 20A breaker?
Only if all the wiring on that breaker is #12 or larger.
> 30A?
Only if all the wiring on that breaker is #10. These are electrical safety code requirements, which carry the force of law.
> 3) Will the Alinco be big enough
Yes
> or should I upgrade that as well?
No.
73, Jim K9YC