[TheForge] Gas heater question
Andrew Vida
osan at netlabs.net
Thu Nov 21 18:06:25 EST 2013
On 11/20/13, 9:19 AM, Paul Sperbeck wrote:
> What pressure is your natural gas delivered at? I needs to be around
> 7" of water coulomb or 1/4 PSI.
Right at 7" coming into the house.
>
> Most appliance regulators can handle the input pressure from natural
> gas, which is normally delivered at 7" of water coulomb, or propane
> which is normally piped inside the building at 11" of water coulomb.
> The appliance regulator will then reduce either of those to about 3.5"
> of water column to supply the jets.
>
> Use the chart to get the size you need:
> http://www.hvacredu.net/gas-codes/module2/Gas%20Orifice%20Capacity%20Chart.pdf
>
That is just what I needed. Thank you Paul. Looks like I will need to
open the existing orifice to a 42.
>
> Use the btu of each propane burner and then look up that btu for
> natural gas and see what size the orifice is.
>
> Your propane dealer may have jets available if he pulled them from a
> conversion and plays well with others...
>
> paul
Thanks again.