[TheForge] Capacity of Electrical wire
Dan Brewer
danqualman at gmail.com
Sat May 20 12:12:14 EDT 2006
Tig welder 80 amp draw
Mill 20 to 30 amp draw
I would put in number 00 wire. Remember to put in a disconnect in where the
machine is tied in. You should probably put in a sub panel and then go from
there. At the sub panel you will need 2 six foot grounds driven in at least
six foot apart. If you shop is metal tie the shop in at several points
also. Look for some "no ox 2". No ox 2 is a protective covering for
electrical connections to ground. The power run should be in conduit
between the meter and the sub panel. Because of the size of the wire it
should be around 3 inch. I would put in a quad out let every 8 feet along
the wall at the 4 feet off the floor. This way no matter where you position
something you have power. If you run the light power in to duplex outlet
hooking up lights will be easier.
Dan in Auburn
-----Original Message-----
From: theforge-bounces at mailman.qth.net
[mailto:theforge-bounces at mailman.qth.net] On Behalf Of Dan Scheid
Sent: Saturday, May 20, 2006 7:33 AM
To: 'Sponsored by ABANA'
Subject: RE: [TheForge] Capacity of Electrical wire
Question is what is the total amps draw? Also do not put the machine or the
welder on the same circuit as the lights
At 125 you have a small volt drop if you don't go the next size wire bigger
Dan
(lost on the east 40)
> -----Original Message-----
> From: theforge-bounces at mailman.qth.net [mailto:theforge-
> bounces at mailman.qth.net] On Behalf Of Jerry Smith
> Sent: Saturday, May 20, 2006 6:56 AM
> To: The Forge
> Subject: [TheForge] Capacity of Electrical wire
>
> I am putting in new service and need to run the lights
> as well as a milling machine, along with a powerful
> TIG welder. What wire do I need to run from the meter
> to my breaker box? This is a 125 foot run.
>
> Thanks,
>
> Jerry
> _______________________________________________
> Manage membership or unsubscribe at:
> http://mailman.qth.net/mailman/listinfo/theforge
> theforge mail list group photo site is
> http://www.photoaccess.com
> Login: blacksmithblacksmith at hotmail.com
> password: anvil
> ___________
_______________________________________________
Manage membership or unsubscribe at:
http://mailman.qth.net/mailman/listinfo/theforge
theforge mail list group photo site is
http://www.photoaccess.com
Login: blacksmithblacksmith at hotmail.com
password: anvil
___________
More information about the TheForge
mailing list