I was thinking along those lines, Geoff, but your confirmation makes it clear. I'll
check the drop when I put the unit into service, and wire it accordingly.
Thank you for your attention.
Arthur

Geoff Greer wrote:

> Hi,
>
>   It seems like the 2 other terminals are sensing terminals.  Unless voltage drop
> across the leads feeding the load is a problem, you can jumper the S+ to the V+ and
> jumper the S- to the V-.  If drop is a concern, the sense leads should be hooked to
> where the supply leads feed to.
>
> Regards,
> Geoff Greer
>
> 5/26/03 15:50:06, Arthur Shulman <[email protected]> wrote:
>
> >The above item has 4 output terminals. V+ & V- are no problem, but the
> >remaining 2 are marked V+S+ & V-S-.
> >
> >What is the correct method of utilizing these terminals? Should V+ be
> >tied to V+S+, & V- be tied to V-S-? If not, from which terminals does
> >one take the 12vdc/13A output?
> >