[Lowfer] power line interference
Charlie , W5COV
cvest at cox.net
Mon Dec 20 14:52:06 EST 2010
I built an ultrasonic receiver with a small hand held parabolic dish and
once you are in the area they are absolutely amazing at getting problems
pinpointed exactly .
Having tagged along with the FCC on a 2 year long noise problem from the
local utility company , I learned a LOT about noise finding . They were here
at least once a month , on the Kansas side of the line in Coffeyville .
Plus I was a consulting engineer for that same power company for 5 years and
had to handle all of the noise complaints . I could write a book on what
causes problems and locating and resolving them .
MOST utilities are very good at working with hams , since if it is there
problem , the ARRL and FCC WILL get involved and stay involved as long as
the problem lasts .
Also the ARRL engineer was here ,along with a well known expert in the field
, that has written a book , so I learned even more modern methods , than
when I used to lug around a Sprague noise interference locator that had a
small loop on it and must have weighed 50 pounds !!
It does sound like the entire crossarm and hardware needs to be rebuilt .
With copper prices what they are , I found half a dozen or more poles with
the ground wire cut off as high as they could reach . So that is an obvious
thing to check .
One thing I don't know how much I agree with , but the expert that the ARRL
brought in , said that all of the ground wire staples could not be metal and
they replaced them with an insulated one .
The insulator certainly needs to be replaced . They also need to check any
other insulators for carbon tracking . A problem that I commonly found .
Also when they replace the insulator another very common problem is the tie
wires . I found that often too , they cause a terrible fuss sound . So have
them replace the tie wires .
Have them tighten EVERY piece of hardware , especially on the crossarms ,
even on adjacent poles .
Also a very common problem on the older lines comes from the clip that they
use on the transformer that you are on and sometimes a pole or two away.
INSIST that they put the new version on that has a bolt to hold it tight ,
instead of the old clips.
Sorry I got carried away , but it is something that I worked with for many
years and still do some consulting on today .
Perhaps this will help other people too .
If I can think of anything else that was common on the distribution lines ,
I will add it later .
Actually about 75 % of the problems that I found were in the surrounding
homes . Fish tank heaters , electric fences that weren't known to the
complaining party , door bell transformers and recently plasma TV's .
Hope this helps someone .
Charlie , W5COV