On 6 Dec 2007 at 20:27, Gudguyham at aol.com wrote:
> whenever I run electrical to new construction, I run only three
> wires > for 220... the two hot sides and the neutral/ground... so
> far the > electrical inspector has signed off all of it with no
> hesitation, even > though I am not convinced the national code is
> being met...
>
> It is not. Perhaps your inspector is not up on the latest
> electrical code. It now requires separate ground and neutral
> wires.
>
>
> If you have a 220 volt ONLY load, like a 220 baseboard heater, or a
> ham amp connected for 220v you only need 3 wires.
Yes.
> 2 hots and a ground.
Notice the word "GROUND" here, not Neutral. They are not
the same thing and serve different purposes.
> A neutral is not needed.
Correct.
> 4 wires
i.e., 2 hots, a neutral, and a ground.
> is needed only when the load uses
> 120v as well as 220, like a stove, clothes dryer and the like. Lou
Or if you have other 120v appliances in the home...like
lights, etc. One reason for the requirement for a neutral is
that in a home, most loads are not evenly balanced across
the 220v line.
Ken Gordon W7EKB