In the 24 volt aircraft systems I worked with power was typically routed
into the cockpit via 1/2" diameter copper rods that ran along behind the
breaker panels. Breakers for each circuit were tapped into the rod with
threaded holes and screw.
That's what it takes to avoid excessive I^2R losses for a system that draws
significant current.
And never lose sight of the danger of a low-voltage high-current system.
First, if you have an inductive load, the pulse that occurs when it's
disconnected can run into many hundreds of volts - enough to do real damage
if you're holding the two ends of the circuit as you disconnect it.
But more commonly is the danger of a short circuit. Things turn red-hot
instantly and even thick bus-bars can melt. I saw a guy drop a screwdriver
into an aircraft 24-volt bus once. I was glad I was 50 feet away in the next
plane. It looked like a bomb went off as the shaft of the screwdriver melted
so fast it literally exploded with a huge bang, showering the poor guy with
molten steel and setting the plane on fire.
I also knew techs missing fingers after getting a ring across a low-voltage
source. The rings heated so fast it welded to the terminals before he could
pull away and the hapless fellow had to suffer the melting metal burning his
finger off until he was able to jerk his hand away without the finger. I
heard of one fellow who wore a metal watch band and, yes, he reportedly lost
his whole hand.
To this day, I remove any jewelry when I'm working around a high-current
low-voltage source like an automobile battery.
Ron AC7AC
-----Original Message-----
From: elecraft-bounces at mailman.qth.net
[mailto:elecraft-bounces at mailman.qth.net] On Behalf Of Edward R. Cole
Regarding high-current dc distribution: I ran into that issue lots
of years ago when I wanted to run some ham gear outside my travel
trailer and use the 12v system as power source. I quickly found that
30-feet of #14 or #12 wire would not do. I finally used a 12v
battery and floated it from the trailer power. And I was only
running 150w on 2m.
At one time I was considering solar power for a two-story log-cabin
in the bush, but the wiring gets expensive (so do the panels). The
cabin now has 120vac utility service so its a moot issue (and I sold
it in 2003).
My present shack has 13.8v provided by 50A Astron which is connected
via a 12-foot run of #6 welding wire to the main 30A buss fuse. This
connected to a heavy barrier terminal strip to provide power to all
the amplifiers and high-current equipment. I see about 13.5v at the
main fuse when running loads; unloaded it shows 13.75v.
Two power leads run from there to two more barrier strips: one is
#12 solid house wire and the other #8. Both about 3-foot long. My
new 144-28 50w transverter runs off the strip fed by #8 wire and
voltage runs at 13.2 under load. My K3/10 is fed from the #12 wired
strip. There are only two other items connected there: panel lights
for my manual antenna tuner and the main station controller (fused at 5A).
Many of my new amps require 28vdc. I have a 8A and two 50A supplies
for 28vdc. One 50A PS runs the 16-foot dish rotator-motors and will
run 432-100w and 1296-300w PA's at the dish. I run #12 romex out
there for 120vac power (remotely switched). The other 50A PS may go
to the base of one tower where I may install some big amps for 900
and 1296 MHz. To place the amps at 50-feet will require #6 wiring up
the tower. Installing a switching PS at tower-top becomes attractive
(not the 90-lb. 50A PS).
Ohms law rules dc-wiring!
Ed
------------------------------