On Sat, 27 Mar 2010 16:09:36 -0400, Tom W8JI wrote:
>> NO! This is a summary of NEC (National Electric Code)
>> requirements: The
>> NEUTRAL of a transformer on the secondary side MUST be
>> bonded to the
>> equipment ground (steel conduit, the green wire, building
>> structure, etc),
>> and that green wire must be carried from the breaker panel
>> to each outlet and
>> to the transformer. The neutral conductor that feeds the
>> primary side of the
>> transformer must be bonded to ground at the service for
>> the building (that
>> is, the main breaker panel). And, as we all know, all
>> groundes must be bonded
>> together. Thus, an isolation transformer does NOT isolate
>> either the neutral
>> or the equipment ground.
>I wonder when that changed? All of my isolation
>transformers, probably manufactured in the 70's or 80's,
>float the mains terminals on the load side. We used them all
>the time working on AC/DC radios and I still use them now
>working on SMPS. Only the case and safety grounds are
>grounded.
I have some UTC or Triads like that too. You can probably get
away with using them on a service bench, but an electrical
inspector would red tag you if you tried to install them
without bonding the neutral. If I'm not mistaken, there also
needs to be a breaker or fuse somewhere.
73,
Jim K9YC