But Jim,
The secondary of an isolation transformer is fully isolated - i.e.
floating AC. The fact that the neutral of the transformer input side is
bonded to the green wire ground is quite a different thing. A proper
isolation transformer has no relationship to neutral on the secondary
side - only the safety ground and the voltage across the secondary winding.
Remember the old AC/DC receivers that had one side of the AC line tied
to the chassis! Every proper service bench had an isolation transformer
during that era.
73,
Don W3FPR
Jim Brown wrote:
> On Sat, 27 Mar 2010 09:32:12 -0400, Don Wilhelm wrote:
>
>
>> An isolation transformer *does* isolate the neutral (and the hot),
>>
>
> NO! This is a summary of NEC (National Electric Code) requirements: The
> NEUTRAL of a transformer on the secondary side MUST be bonded to the
> equipment ground (steel conduit, the green wire, building structure, etc),
> and that green wire must be carried from the breaker panel to each outlet and
> to the transformer. The neutral conductor that feeds the primary side of the
> transformer must be bonded to ground at the service for the building (that
> is, the main breaker panel). And, as we all know, all groundes must be bonded
> together. Thus, an isolation transformer does NOT isolate either the neutral
> or the equipment ground.
>
> What an isolation transformer DOES do is reduce the voltage between neutral
> and ground to zero. It also shortens the return path for leakage currents on
> the green wire -- they now return to that transformer, not to the more
> distant breaker panel at the service entrance. This has the potential to
> reduce noise current on the shield of signal cables. BUT -- the simple
> bonding regimen outlined in my Ham Interfacing Power Point is a MUCH less
> expensive AND more effective solution.
>
> 73,
>
> Jim Brown K9YC
>
>