[Elecraft] Was Grounding negative side of power supply? - CORRECTING A SERIOUS ERROR
Jim Brown
jim at audiosystemsgroup.com
Thu Jan 21 12:42:01 EST 2010
NO, NO, NO!
Joe, who rarely ever gets it wrong, has led us down a VERY wrong path,
and you, who also rarely get it wrong, have followed him. :)
It is the NEUTRAL that must be bonded to EARTH and SYSTEM GROUND at the
main panel/service entrance, and ONLY at that panel. An additional
NEUTRAL connection to ground (or the green wire) is what causes an unsafe
condition.
Multiple paths to earth for the chassis of equipment are a GOOD thing, as
long as they are all bonded together. in fact, safety codes and good
engineering practice all say that you can have as many connections to
EARTH as you want, that more connections are better, AND that all of
these earth connections MUST be bonded together by a low impedance path.
On Wed, 20 Jan 2010 22:46:54 -0500, Don Wilhelm wrote:
>Joe and all,
>I would also like to point out that the situation Joe presents can be
>the source of "sneak ground path currents" which can contribute to noise
>at your station.
I suggest study of my power point on Ham Interfacing to understand what
you are calling "sneak ground path currents" -- indeed, they are nothing
more than leakage currents from the hot side of the AC power line through
capactance to the chassis of equipment. This capacitance includes bypass
capacitors (including those in line filters) and the stray capacitance
between the power transformer primary and its frame, which is bonded to
the chassis.
http://audiosystemsgroup.com/HamInterfacing.pdf
For more on power and grounding, see
http://audiosystemsgroup.com/SurgeXPowerGround.pdf
>By all means, connect any ham related ground rods to
>the AC mains entry point ground rod. I don't care how you accomplish
>that - just "do it". If it reduces noise in your receiver, that is a
>benefit, but if not, be assured that your shack will be a more safe
>place to inhabit.
YES!
>73,
>Don W3FPR
>Joe Subich, W4TV wrote:
>> This creates a situation that is potentially hazardous
>> to your equipment. The AC "third (green) wire" is supposed
>> to be connected to ground only at the main panel/service
>> entrance.
WRONG. See above.
73,
Jim Brown K9YC