[Elecraft] Grounding negative side of power supply?

Don Wilhelm w3fpr at embarqmail.com
Wed Jan 20 22:46:54 EST 2010


Joe and all,

I would also like to point out that the situation Joe presents can be 
the source of "sneak ground path currents" which can contribute to noise 
at your station.  By all means, connect any ham related ground rods to 
the AC mains entry point ground rod.  I don't care how you accomplish 
that - just "do it".  If it reduces noise in your receiver, that is a 
benefit, but if not, be assured that your shack will be a more safe 
place to inhabit.

73,
Don W3FPR

Joe Subich, W4TV wrote:
> This creates a situation that is potentially hazardous 
> to your equipment.  The AC "third (green) wire" is supposed 
> to be connected to ground only at the main panel/service 
> entrance.  However, since it is connected to the chassis 
> of the power supply, it is also connected through the power 
> supply and radio to ground via the coaxial cable. 
>
> If the point at which the coaxial cables enter the building 
> is not the same place that power enters the building, any 
> nearby lightning strike can set up a significant difference 
> in voltage between the power line "safety ground" and the 
> RF ground (feedline shields/tower).  That difference can 
> fry any electronics connected to both "grounds." 
>
> There are techniques for dealing with this problem ... but 
> they are not necessarily easy or inexpensive. 
>
> 73, 
>
>    ... Joe, W4TV 
>   
>
>  
>
>
>   
>> -----Original Message-----
>> From: elecraft-bounces at mailman.qth.net 
>> [mailto:elecraft-bounces at mailman.qth.net] On Behalf Of Don Wilhelm
>> Sent: Wednesday, January 20, 2010 8:01 PM
>> To: David Woolley (E.L)
>> Cc: Rich; elecraft at mailman.qth.net
>> Subject: Re: [Elecraft] Grounding negative side of power supply?
>>
>>
>> The AC side should always be connected to the power supply chassis - 
>> unless it is of the "double insulated" design where no ungrounded 
>> metallic part can come into contact with the human body.  
>> Yes, cutting 
>> the AC "green wire ground" is a dangerous thing indeed - the entire 
>> chassis could rise to the AC mains voltage in the event of a fault.
>>
>> The power supply negative *can* certainly be floating *if* 
>> the designer 
>> made provisions for doing that.  It requires that all the common 
>> connections on the secondary side of the transformer are 
>> isolated from 
>> ground.  As I recall, Astrons are not built that way.
>>
>> 73,
>> Don W3FPR
>>
>> David Woolley (E.L) wrote:
>>     
>>> Rich wrote:
>>>   
>>>       
>>>> I had a situation with an older (analog) power supply 
>>>>         
>> (that had its 
>>     
>>>> negative side grounded to the main AC ground) that tripped 
>>>>         
>> the Ground 
>>     
>>>> Fault Circuit Interrupter (GFCI) in one of the bathrooms.  
>>>> Eliminating the bond to ground
>>>>     
>>>>         
>>> I consider this dangerous advice.  If you have an ELCB 
>>>       
>> tripping, you 
>>     
>>> do
>>> not treat the problem symptomatically, by creating an 
>>>       
>> unsafer system, 
>>     
>>> you find out what the real problem is and you fix it.
>>>
>>> I can't tell what the exact wiring configuration is here, but it is 
>>> very
>>> likely that you have created a situation where there are 
>>>       
>> pieces of metal 
>>     
>>> in reach which have low impedance paths to very different "earths".
>>>   
>>>
>>>       
>> ______________________________________________________________
>> Elecraft mailing list
>> Home: http://mailman.qth.net/mailman/listinfo/elecraft
>> Help: http://mailman.qth.net/mmfaq.htm
>> Post: mailto:Elecraft at mailman.qth.net
>>
>> This list hosted by: http://www.qsl.net
>> Please help support this email list: http://www.qsl.net/donate.html
>>     
>
> ______________________________________________________________
> Elecraft mailing list
> Home: http://mailman.qth.net/mailman/listinfo/elecraft
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Elecraft at mailman.qth.net
>
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
> ------------------------------------------------------------------------
>
>
> No virus found in this incoming message.
> Checked by AVG - www.avg.com 
> Version: 9.0.730 / Virus Database: 271.1.1/2634 - Release Date: 01/20/10 04:12:00
>
>   


More information about the Elecraft mailing list