[Boatanchors] Basic electricity question
WA5CAB at cs.com
WA5CAB at cs.com
Thu Jan 13 23:16:50 EST 2005
Gary,
Well, I think you were speaking theoretically and I was speaking from
practical experience (and Code requirements). A perfectly balanced three-phase
system even if Wye connected would have no current flowing in the neutral and you
could save 20% on copper costs plus nearly that much on conduit diameter costs
and dispense with the neutral. There was for example no neutral on our
compressor pad because it was Delta to Delta and the controls were on another
system. But in most practical situations, commercial three phase end-user systems
are a mix of single and three phase loads. So you usually do need the neutral.
If you don't have it, you may end up with the same situation as happens if
you lose the neutral in a 120/240 volt single phase system. The side (or
phase) with the heavier load will be starved for voltage and the side (or phases)
with the lighter load(s) will get real bright (for a little while). Been
there, done that, we couldn't afford tee-shirts because of the cost of the
equipment destroyed. :-)
In a message dated 1/13/2005 9:33:36 PM Central Standard Time,
garyschafer at comcast.net writes:
> Hi Robert,
>
> I thought I was covering all my bases. I did say "no neutral required". :>)
> But, if a neutral is used in a Y 3 phase then the part of the load that
> uses the neutral is not a 3 phase load but a single phase load. :>)
>
> 73
> Gary K4FMX
>
Robert Downs - Houston
<http://www.wa5cab.com> (Web Store)
<wa5cab at cs.com> (Primary email)
<wa5cab at houston.rr.com> (Backup email)