Hello Wayne,
Connecting transformers back-to-back is not a good long term solution. The
transformer designer calculated how much extra beef the primary needed to
provide magnetising current for the core. For the transformer in the second
position, when you use the secondary as the primary, all that magnetising
effort must come from the secondary, which it was not designed to provide.
So, the second transformer will overheat.
Still this is wonderful news for American transformer manufacturers.
Already, in my experience, the accountants have shaved the amount of copper
and iron very close to the bone; so, American transformers run much hotter
than ones designed by engineers. And because you will burn out the second
transformer you will need another = extra sales. Isn't that just wonderful?
73 de Brian, VK2GCE.