On 19 Feb 2015 at 20:17, Bruce Long via ARC5 wrote:
> The breaker tripping at no load might be in-rush current but if that is the case
> it should only trip the breaker - say- 1 out of three times.
Yes. Exactly. And that is what happened with mine: about 1/3 to 1/2 the time.
> If you close the
> power switch at the peak of the 60 Hz sine wave peak, the in-rush current will
> be very small. Large in-rush currents happen when you close the power switch
> near the sine wave zero crossing point when voltage is at a minimum --- no I did
> not get that wrong, power on at V=zero is the worst case.
Yup. :-)