[TheForge] 5HP electric motor advice sought
Paul Novorolsky
crosspein at sbcglobal.net
Sun Jul 27 10:35:04 EDT 2008
Ooops, made a typo. Below I said OK to put 10ga wire on a 30amp circuit.
What I meant was it's OK to put 10ga wire on a 20 amp circuit.
(Actually, I've done that for longer runs, to reduce the voltage loss)
Paul Novorolsky wrote:
> Mike,
> I only have a partial response, and I'm not very motor literate, but I
> do have electrical experience, so I only addressed the circuit
> capacity. (and probably in more detail than you wanted anyway)
>
> Horse power can be converted directly to watts (and therefore current
> capacity)
>
> A 5 HP motor is 3728 watts. (About 745.7 watts/hp). However, that is
> OUTPUT power, not input. The motor gives off heat, so it will require
> more than that to drive it.
>
> (I often use a 750 watt / hp for a quick "in my head" calc for motor
> ratings. A motor that is advertised as 1hp, but is only rated for 5
> Amps at 120VAC is NOT a 1 HP motor.)
>
> So at 230 V (3738 / 230 ) that's about 16 Amps, so the motor draws at
> least that much.
>
> So the 23 Amps may include a startup surge, or perhaps that is the
> steady draw. (I'm not sure how the switch was rated)
>
> At any rate, 12ga wire is rated for 20Amps. So you may either exceed
> the rating briefly during startup, or it may be dangerous to run it.
>
> The key here will be your breaker. Even if the current only exceeds 20
> amps briefly, it may trip some of the time.
>
> One thing you don't want to do is combine a bigger breaker than the
> capacity of the circuit (wiring) that it is to protect. Otherwise, the
> wiring may get hot enough to start a fire. So my advice for this piece
> is go to a 30 Amp breaker and 10 ga wire. (You can put 10 ga wire on a
> 30 amp circuit, but never put an under-rated wire on a smaller circuit
> breaker. That is a 30 Amp breaker with 12ga wire is dangerous)
>
> Motor starters (at least "in the old says") were basically centrifugal
> switches. They engage the starter winding, and once the motor spins
> up, the centrifugal force operates the switch, and the motor switches
> off the starter winding and runs on the main winding alone. That's
> probably all I know about it.
>
> **paul
>
> Mike Spencer wrote:
>> I need some ignorance-removal re. a 5 HP motor. If that's nothing you
>> know about, you can stop here and skip the boring details.
>> I bought a 5 HP, capacitor start, 230V, (marked "23 amps" and 1.15
>> service factor) motor. It has a big junction box with 4 capacitors of
>> one kind, two of another kind and some sort of magnetic switch. Shaft
>> is 1-3/8". I replaced a capacitor that was arcing, swapped wires
>> around to get the right direction of rotation. For testing purposes,
>> it's hooked up:
>>
>> 230V welder outlet
>> |
>> 20' of 12 ga. wire
>> |
>> Heavy spring-loaded manual switch
>> |
>> Motor line cables
>>
>> In that configuration, it starts smoothly and runs fine with no load.
>> But I have questions before I stick it on my compressor:
>>
>> 1. Is my existing 12 ga. wire okay for 5 HP/23 amps in a 30' run? Or
>> should I have 10 ga. or even 8 ga.? The piece of line cable dangling
>> out of the motor is 8 ga.
>>
>> 2. Is my Square-D 9013GHG pressure switch going to work? Fuzzy
>> markings inside (apparently in Spanish) seem to indicate that it's
>> only rated for 3HP at 230V single-phase and 5HP 3-phase (if that
>> makes any sense.)
>>
>> 3. There's some kind of thing called a "starter". Do I need one?
>> What does it do? If I need one, how do I wire it up so that the
>> pressure switch takes advantage of whatever the "starter" does?
>> Or do I need a pressure switch that is also a "starter"?
>>
>>
>> The compressor is rated 400 PSI. I only run up to 150 PSI and the
>> pressure switch cuts in again at -- I forget, 90 PSI?. Original 10HP,
>> 3ph motor was 3250 RPM with a 4" sheave. Present motor is 2 HP, 3250
>> RPM with the same 4" sheave. This new 5 HP motor is 1725 RPM and I was
>> planning to put an 8" sheave on it to get the same RPM at the
>> compressor. This will, I'm thinking, increase the starting current in
>> the motor but I don't know if it's enough to matter.
>>
>> I downloaded a 4.5 meg PDF from Square-D that gives every imaginable
>> mechanical engineering spec for 9013-series pressure switches *but
>> not* their current-carrying capacities or electrical specs. Feh.
>>
>> Any advice or answers welcome.
>>
>> Thanks,
>> - Mike
>>
>>
> _______________________________________________
> Manage membership or unsubscribe at:
> http://mailman.qth.net/mailman/listinfo/theforge
> theforge mail list group photo site is
> http://www.photoaccess.com
> Login: blacksmithblacksmith at hotmail.com
> password: anvil
> ___________
>
>
>
More information about the TheForge
mailing list