[TheForge] Propane supply problem
terry l. ridder
terrylr at blauedonau.com
Thu Jul 8 22:51:00 EDT 2004
hello;
On Thu, 8 Jul 2004, Marc Godbout wrote:
marc> Thanks for all the input from everyone so far. I did try to get help
marc> from our fire marshal, who is the code enforcement officer in this
marc> subject. He never stated that anything was against code, but was
marc> unwilling to advise on anything higher than 10 psi because he found no
marc> references or charts going higher than that. Mostly it sounded like
marc> weasel-wording to avoid liability.
marc>
as noted previously he is not the "authority having jurisdiction" in the
sense it is used in the nfpa 58 code.
marc>
marc> Terry, would you have any reference to flare connections not being good
marc> over 5psi? I need to hunt again, but I did find some reference to flare
marc> being good at much higher pressures. I only remember it was from a
marc> Canadian website.
marc>
i will dig up the references later this evening.
marc>
marc> I could probably be the "authority", but I don't meet the other
marc> requirements. I wouldn't trust my meager welding skills to something
marc> like this. Maybe I could qualify as a research facility. After all, I'm
marc> constantly learning something new :-)
marc>
you are the "authority having jurisdiction" and site the nfpa code 58
defintion and note if asked.
blacksmithing is "industrial processing" therefore meets at least one
the the criteria. the question would be is it exclusively used for
blacksmithing. research would be an alternative, you are researching "the
plastic deformation of various metal alloys heated to varying
temperatures."
<begin quote>
2.5 piping system operating pressure limitations
2.5.1 maximum design operating pressure
the maximum design operating pressure for a piping system located inside
buildings shall not exceed 5 psig ( 34 kpa gauge ) unless approved by
the authority having juridiction and one or more of the following
conditions are met:
(a) the piping system is welded.
(b) the piping system is located in a ventilated chase or otherwise
enclosed for protection against accidental gas accumulation.
(c) the piping is located inside buildings or separate areas of
buildings used exclusively for:
1. industrial processing or heating. (<--- notice )
2. research
3. warehousing, or
4. boiler or mechancial equipment rooms.
(d) the piping is a temporary installation for buildings under
construction.
<end quote>
marc>
marc> Methinks I'll stick with the 5psi and play with the burners some more.
marc> That seems to work for enough people, so why not me? My only problem may
marc> be oxy-propane cutting, but I could get around that with a small BBQ
marc> tank, if need be.
marc>
marc> --Marc
marc>
--
terry l. ridder ><>
More information about the TheForge
mailing list