[Test-Equipment] DC Breaker switches

Rasputin Novgorod priapulus at yahoo.com
Sun Jul 5 16:10:09 EDT 2009


Gentlemen:

Besides test gear, I'm also a Ham (radio amateur) so have
a bunch of 12 dc powered radios. I recently got a bunch of
(Telco surplus) DC breaker switches.

I mounted two 75-amp and twenty 30-amp breakers in a
19 inch rack panel. I ganged all the breaker line (inputs)
to a common copper buss bar. 

The load(!) side of the two 75-amp breakers go to a 75 amp
12vdc power supply, and battery (for backup), respectively.
The load side of the 30-amp breakers go to various loads.

By reversing the line and load connections on the two 75-amp
breakers, the breakers could all use a common buss, making a
tidy, elegant installation.

~BUT~ a fiend (sic) of mine saw what I'd done and had a fit.
He said that you cannot reverse the load and line connections
on a DC breaker switch; terrible things will happen. When I
look inside a DC breaker, there is just a coil in series with
a spst switch. If enough current flows thru the coil, it 
magnetically trips the switch.

I can't see why polarity or line/load could make a difference.
So I query the group:

1) Does it matter if I reverse the load and line connections?

2) The breakers are rated at 80vdc and I'm using 12vdc;
will that change the trip rating of the breaker?

The breakers are Heinemann 30 amp, trip 37.5, volt: 80vdc.

Actually, the protection is redundant, as the power supply,
battery and loads are all fused. I'm using the breakers as
switches (because I had them, cheap) to control various loads.
The breaker protection is a nice bonus protection/isolation
of a dead short in a load line.

Sincerely
/blair