[R-390] Isolation transformers [WAS: Corcom...]
Charles Steinmetz
csteinmetz at yandex.com
Fri May 16 19:19:10 EDT 2014
Bill wrote:
>It is still a good idea to ground the frame of the R-390 to Earth so the
>antenna current can go somewhere, unless you are using a balanced
>antenna.
Not just for the antenna, but for electrical safety as well. An
isolation transformer should have a "pass-through" ground -- the
third prong should be continuous from the radio to your house ground,
but NO PART OF THE ISOLATION TRANSFORMER should be connected to it
(except the neutral wire to the primary, but that is done at your
service entrance, not inside the isolation transformer cabinet -- see below).
That is the difference between using an isolation transformer and not
using one. One side of a US 120v mains supply (the neutral) is
connected to your house ground at or near the service entrance, so
there is a current path from the grounded radio chassis to your house
ground. If all is well, no current flows in this path because the
voltage at both ends is the same or very, very close to it. But if
something goes wrong, current CAN flow in this path. Since there is
no such path from the secondary side of a properly wired isolation
transformer, no current can flow in it even if something does go wrong.
So -- what is the safety reason for the pass-through ground? Because
you might knock over a lamp, break the bulb, and have the hot wire
touch the radio chassis. Or, possibly more likely for a ham or SWL,
a falling tree could take out your antenna and a power line, and
connect them to each other. Or your antenna could be hit by
lightning. If the radio chassis is grounded, you are protected (to
the same extent fuses and GFIs protect you in normal
circumstances). If the radio chassis was not grounded, that current
could flow through you and add "SK" to your call sign.
Best regards,
Charles