[PVRCNC] Re: [PVRC] Lightning protection
Bill Tippett
btippett at alum.mit.edu
Fri Jul 29 11:17:08 EDT 2005
At 10:30 AM 7/29/05, you wrote:
>Hi Bill,
>The equipment was not connected to the AC line, antennas or telephone
>lines. The 110VAC to the input to Isobars was removed from the wall
>outlet. The output coax from the Ten-Tec amp was just laying on the
>floor, about a 6' RG-8 cable. I left all of the intra cabling between
>the equipment connected.
>
>We had a discussion in the FL area concerning huge surge currents coming
>in via ground connections thus I had removed all equipment connections to
>my local 10' copper ground rod.
>
>The Ten-Tec 425 amp input PC board had a big burn mark on the PC board.
>This input was connected to the FT-990 output via a 4' lenght of RG-58.
>The FT-990 seems to be OK.
>
>Now in all of this equipment which was just sitting on the desk together
>the following was damaged. The W1GEE serial I/F between the radio PC and
>FT-990, the Astron 35 amp power supply appears to have had a small
>regulator IC blown, in my HB Idiom press keyer, a 78L05 regulator was
>blown. Moreover, all memories in the FT-990 were at their default state.
>
>On the other side of the room my Dell PC was totally disconnected and the
>modem was blown. Interesting enough, I had left a telephone and answering
>machinc connected to the tel. line and they were blown. I forgot to
>removed my xyl's PC connection to the tel. line and that modem
>survived. The PC was not connected to the AC line.
>
>I am glad that you have been so fortunate !!!!! This is the second time
>for this to have happened in a five year period.
>
>My question is now would I really be better off keeping the ground wires
>on the gear? All coax cables shields entering the shack are grounded at
>the point of entry.
>
>Any suggestions or comments are welcome.
>
>73
>Jack, W3TMZ/4 near the Gulf in Central FL.
Hi Jack,
Wow!...but a couple more questions:
1. I assume the phone line was not connected to
your radio equipment in any way. I think that's
correct but just wanted to confirm.
2. How far away is your tower from your shack?
If the problem was induction from a
very close strike, the prudent thing would be
to disconnect all potential "antennas" that could
pick up any induction. I would also disconnect
the equipment from any ground...i.e. no connections
AT ALL. Apparently even your 6' of RG-8 was enough
of an antenna to pick up what apparently was an
extremely close strike. I may not be having problems
because my most likely tower to be hit (180' with
nothing on top) is about 300' away. I have another
~100' high about 150' away but the Yagi's on it
seem to dissipate charge build-up (although
it has been hit at least once to my knowledge).
If, as I am assuming, your tower is quite
close to your shack, the only solution may be
to completely disconnect all interconnections
that can serve as pickup antennas. I have often
heard our house wiring "click" with nearby strikes
which I assumed was internal house wiring induction
(since the service entrance has a surge suppressor
at the meter). We have never had any damage
other than losing an unprotected DirecTV phone
modem (I forgot about that one when installing phone
line surge suppressors!)
I thought I was being very prudent, but
now you make me wonder about even removing
interconnections!
73, Bill W4ZV
More information about the PVRCNC
mailing list