I think there is a wiring problem or shorted power line filter in the
power supply if it has one. A good size transformer will have a
surprisingly low DC resisitance on the primary. Is there any chance the
hots are mistakenly connected to the neutral, ground, or each other?
You should not read a low resistance between the hot pins of the power
cord when the input breaker is off. If you remedy that and the tripping
continues, check the 120/240 volt connections on the primary of the
transformer.
Bruce KA2IVY
On 2/1/17 6:56 AM, JEFF CICCONE wrote:
>
> folks. i have the big heavy 50a 24v dc power supply. i wired it up
> for 230 volt. when i plugged it in it tripped the breaker. when i
> checked the resistance between the 230v input with the circuit breaker
> on the unit open it was ..2 ohms. when i closed the breaker, same
> reading. i'm just wondering if i'm picking up the coil or something
> else. any ideas? thanks. jeff ciccone kg2bz
>
>
>