Yes, inductance limits short circuit current. Been there. Another solution
is to put fuses in the PRIMARY of the transformer. This has two advantages:
The fuse is in it's natural environment, low voltage and AC. He may have to
use slo-blow fuses to ride through the transformer inrush current.
Richard, AA1P
I've nevefr heard of this approach being used to limit SC current in
> electronic equipment before but you can consider what the electric
> utilities
> do to limit current through large distribution power transformers.
>
> I work for our local electric utility company and we are working with
> a
> large commercial customer that wants to connect a sizeable generator to
> our
> network to power their much of their equipment load (using all of their
> generator output) and use our lines to supply the remainder. Our
> load-flow
> studies showed that our circuit breakers would become overdutied if a
> fault
> were to occur on our lines while their generator was operating. So we are
> going to install reactors (no, not that kind, but choke coils) in the
> secondaries of our substation's transformers feeding this customer's
> circuits. The rapid rise in current during a fault will produce a
> high-impedance point at the chokes in the secondaries, thus limiting the
> SC
> current and protecting the transformers.
>
> You might try placing some amount of inductance (RF choke?) in the
> transformer secondaries. I can't help you with an inductance value, but
> it's worht considering and researching.
>
>
> 73 de
> Gene Smar AD3F
>