[Johnson] AC Circuit Wiring Question
Bry Carling
bcarling at cfl.rr.com
Mon May 28 20:59:07 EDT 2012
I can tell you from bitter experience you don't want to put a freezer on one of those ground fault interrupter things.
--
Sent from my android "relatively smart" phone. Please excuse my brevity.
_____________________________________________
From: Ed Tanton <n4xy at comcast.net>
Sent: Mon May 28 20:46:35 EDT 2012
To: 'Tom Bates' <tlbates at lr.net>, EF Johnson Reflector <johnson at mailman.qth.net>
Subject: Re: [Johnson] AC Circuit Wiring Question
I would like to be sure I understand (or learn correctly) what we are
saying:
1) The white neutral wire should not be connected except as 1/2 the
leg for 120VAC fans? Or do they go from 1/2 leg to ground?
2) The ground wire IS connected to ground;
3) The 220VAC is on the remaining two wires-120VAC/side-I found a
pretty good set of drawings at:
http://www.do-it-yourself-help.com/wiring_receptacles.html
Ed Tanton
website: http://www.n4xy.com
All emails <IN> & <OUT> checked by
Norton AntiVirus with AutoProtect
_____________________________________________
Wag more / Bark less
_____________________________________________
///snip
>>What is done with current appliances, stoves, dryers, etc.?
Probably an understading of the terms for the conductors would be helpful.
When one speaks of the "neutral" conductor, he is referring to a current
carrying conductor. This would also be the "identified" conductor or
"white" wire, and is "grounded" to earth back at the service. That's also
why it is called the "grounded" conductor. In years past, the Natl
Electrical Code allowed the bare stranded conductor on some cables to be
used as both a "grounded" neutral conductor and also a "groundING" conductor
on some 120/240 3 wire circuits (very commonly seen as 30Amp 3 wire plug on
dryers and welders and 50 Amp 3 wire plug on electric stoves). Now days, a
4 wire plug is required on those split circuits. That's those circuits
(like a clothes dryer) that utilize 240 Volts for the heating elements and
120 Volts for the motor and controls.
So, simply put--The neutral or ground-ED wire is normally a white insulated
current carrying conductor while the ground-ING wire (usually insulated
green or bare) is used as a safety wire connecting equipment metalliac parts
directly to ground and only carries current if there is a fault.
Take Care,
Tom - AA1NZ
///snip
_____________________________________________
Johnson mailing list
Home: http://mailman.qth.net/mailman/listinfo/johnson
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Johnson at mailman.qth.net
This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
More information about the Johnson
mailing list