Current NEC code requires L1, L2, Neutral, and ground for 240 volt
residential service. That's 4 wires. Neutral and Ground are to be
connected to a common buss bar only at the main circuit breaker. To the
best of my knowledge all local codes do accept a driven ground with less
than 20 ohms resistance located at or below the service entrance. Most
residential electric services no longer recognize connection to the water
line as adequate ground due to the use of plastic pipe or "current breakers"
being and insulated section of line to prevent currents flowing and
subsequent electrolysis of the water lines or water mains. Further, NEC
code requires that all driven grounds for equipment served by a common
electric service must be bonded together.
Now for hams this likely gets to be a sticky wicket. Yes, your driven
ground for your station or your tower or your antenna system must be bonded
{i.e. connected} via a hard conductor back to the service entrance ground in
order to comply with NEC code. Now what happens if it is not done that way.
Well in the event of a fire, thus loss of the structure, and the insurance
fire investigator finds such installation exists, it is likely that your
insurance company will simply thank you for your business. Otherwise, we'll
see you in court and you, the homeowner, should expect to loose.
The 240 volt service is split thus providing two 120 volt sources with the
phase between the two being 180 degrees. Thus the neutral will carry any
difference in current identified by the two lines, L1 and L2. Thus if L1
has a 10 amp load and L2 has a 12 amp load the neutral will have 2 amps of
current, power factor not withstanding. At the same time, a 240 volt load
connected between L1 and L2 will not have any effect on neutral current,
again power factor not withstanding.
At the same time, NEC does acknowledge the "grandfather clause" {I forget
the date} in that older residences are considered safe with L1, L2 and
Neutral with neutral being the common ground point.
73
Bob, K4TAX
----- Original Message -----
From: "Rick Brashear" <rickbras at airmail.net>
To: <heathkit at mailman.qth.net>
Sent: Thursday, December 06, 2007 4:21 PM
Subject: RE: [Heathkit] Gadzooks, when is a ground a ground?
That's the way I understand it too, Larry. You should never use the neutral
for the ground wire either in a 120 vac setup or a 220 vac setup. Like you
said, it defeats the entire concept of the ground.
Rick/K5IAR
While all of this seems correct, my input is that these grounds do not take
the place of the neutral wire.
If the 220V is used to derive two separate 110 volt lines, the neutral needs
to be carried with the 220 volt line.
The Ground is separate. The grounds will be connected to a common point,
usually at the service entrance panel,
it would scare me to wire a house without the neutral being carried in
addition to the ground. If the integrity
of the neutral is compromised, the 110 volt lines can measure a lot
different than what is expected.
Just my opinion. Thanks
Larry N7LB
_______________________________________________
List Administrator: Duane Fischer, W8DBF
** For Assistance: dfischer at usol.com **
$$ See the vintage area on the HCI web site - http://www.w9wze.org $$
Heathkit mailing list
Heathkit at mailman.qth.net
http://mailman.qth.net/mailman/listinfo/heathkit
More information about the Heathkit
mailing list