On 4/23/2020 7:27 AM, N4ZR wrote:
> I used a 3/4" copper water pipe along the back edge of my desk, with a
> short pigtail of #2 wire to the K3.
#2 ????? That's FAR larger than needed for bonding inside the shack.
Also, remember that lightning is an RF event, not a DC event, so
inductance dominates the bonding impedance. #10-#12 stranded is plenty
good enough for bonding between your gear and that bonding bus.
73, Jim K9YC