On 5/18/2019 4:28 PM, Clay Autery wrote:
> 230VAC on 3 wires? Never knew they did 3 wire 220V.... I always
> assumed it was still 2 hots and ground (plus an optional neutral).
In distribution service 240V "single phase" is two "hots" (usually
black/red)plus neutral (usually white), with a physical ground electrode
(ground rod or equivalent) at the transformer and another ground
electrode at the CSED (Customer Service Entrance Device - a fancy name
for the meter plus main disconnect). Those grounds do not carry load
current, only fault current. Three-phase distribution obviously has
three "hots" (usually black/red/blue) with neutral only if it is
120/208V wye or one of the phases of a 240V delta service is tapped for
120/240 single phase service. Separate grounds still apply.
73 de K2ASP - Phil Kane