Just because the Specification says 20 amps, that is the maximum current 
draw for the amp - it does not say that the breaker must be 20 amps, 
only that it must be 20 amps or higher.
A 30 amp breaker is fine if the wire is #10 or larger.

Think about what you normally plug into a 120 volt 15 amp receptacle - 
does it always draw 15 amps?  Certainly a hair dryer might, but your 
cellphone charger does not.