I do not understand the need for three wires plus ground. For a clothes dryer outlet a neutral is required to get 110VAC from one of the phases to the neutral. But for amps you only need both phases and a ground. The plugs are three wire, not four.
73,
N2TK, Tony 

-----Original Message-----
From: elecraft-bounces at mailman.qth.net [mailto:elecraft-bounces at mailman.qth.net] On Behalf Of Jim Brown
Sent: Monday, July 09, 2018 8:40 PM
To: elecraft at mailman.qth.net
Subject: Re: [Elecraft] Breakers for KPA1500?

On 7/9/2018 12:26 PM, Bob McGraw K4TAX wrote:
> I would also suggest using three -  #10 with ground as the line from 
> the breakers to the amp operating position.

Not only a suggestion -- it's the law! Electrical Codes carry the force of law, and they require that the equipment ground must 1) run with the current carrying conductors and 2) must be no smaller than the largest conductor.

73, Jim K9YC