On 7/9/2018 12:26 PM, Bob McGraw K4TAX wrote:
> I would also suggest using three -  #10 with ground as the line from 
> the breakers to the amp operating position. 

Not only a suggestion -- it's the law! Electrical Codes carry the force 
of law, and they require that the equipment ground must 1) run with the 
current carrying conductors and 2) must be no smaller than the largest 
conductor.

73, Jim K9YC