If wire run ends up being 50' you could see a 2V drop at 13A. Agree that switching supply in amp won't care. 26W of heat in the wire inside a wall would bug me.
73
Josh W6XU
Sent from my mobile device
> On Jul 9, 2018, at 3:12 PM, Roy Koeppe <k6xk at ncn.net> wrote:
>
> The KPA1500 uses a regulated power supply: input 195 to 250 vac. Voltage loss in #12 wires is so small the regulator will laugh at that.
>
> 73, Roy K6XK
>
>
> "I would also suggest using three - #10 with ground as the line from the
> breakers to the amp operating position."
>
> 73
>
> Bob, K4TAX
>
>
>> On 7/9/2018 11:43 AM, Roy Koeppe wrote:
>> Yes, that is what I am using.
>>
>> 73, Roy K6XK
>>
>>
>> I probably missed this but my google searches aren't working either.
>>
>> Will 2x 20A breakers (220v) be sufficient for the KPA1500?
>>
>>
>
>