On 4/28/2018 4:55 PM, Don Wilhelm wrote:
> Unless the wiring route is short, take Jim Beown's (K9YC) advice about
> conductor sizes. Large conductors are not required for the current
> draw, but oversize wire will help reduce the voltage drop when current
> is drawn.
That's why, for one of the mountain-top comm sites that we designed for
a desert site out in the middle of nowhere, we specified - ready for
this - 900 Kcmil conductors (*) for a 120/208V 400A feeder because the
power company located the CSED (Customer Service Entrance Device) i.e.
meter and main breaker installation - at a point down the hill that
they could reach in any weather.
(* Visualize copper-filled garden hose. 3 sizes over minimum code (4/0
AWG) to minimize voltage drop and conductor heating.)
73 de K2ASP - Phil Kane