On 9/9/2017 10:43 AM, Doug Hensley wrote:
> I'm was pleased to hear K3, K3S & KX3 owners consistently reporting whatever hash their units were producing had no ill effects on their Elecraft radios during the period their generator was running.
It is quite common for generators to produce RF noise that radiates on
power wiring and is received by nearby antennas. The solutions are 1)
bonding the frame of the generator to the house ground with short, fat
copper and/or 2) a serious multi-turn ferrite common mode choke on the
cable from the generator output, as close to the generator as possible.
Obviously, proper bonding of all grounds is critical to #1 working.
Square footage of a home affects the electrical load ONLY if the
generator must run HVAC an system, and the load of that system is likely
to be MUCH greater than everything else put together, except a well
motor. A larger generator is likely to put out more RFI and be more
difficult to suppress.
73, Jim K9YC