I agree with Joel on this.  I have a 220 socket, but ordered the 120 v model as I wanted to be prepared to move to another location where the 220 volt outlet wouldn't be possible.  I have had zero issues with the dedicated 120 outlet, also with 12 Ga. stranded, dedicated to 20A breaker.

73,
Bill
K9YEQ

-----Original Message-----
From: elecraft-bounces at mailman.qth.net [mailto:elecraft-bounces at mailman.qth.net] On Behalf Of Joel Hallas
Sent: Monday, October 30, 2017 5:06 PM
To: elecraft at mailman.qth.net
Subject: Re: [Elecraft] KPA-500 on 120 V

Yes, the KPA500 can be set up to run efficiently on 120 V vs 240. 

OTOH, as many have correctly noted, it will work much better with a dedicated 20 A circuit using #12 AWG wire. Recognizing that, I figured it was not much more trouble to put in a 240 V 20 A circuit with #12 wire (ok,
4 instead of 3 wires, per current code). If you have the space in your CB box for the proper dual breaker, the effort is almost the same -- but you get two benefits:

1. The voltage drop, and perhaps more importantly the change in voltage drop from key up to key down, is about half -- much better for everybody, and more peak output, if you're counting.

2. You now have the wiring in place for the KPA-1500, should you be so inclined some day. 

Regards, Joel Hallas, W1ZR
Westport, CT




______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft at mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message delivered to k9yeq at live.com


More information about the Elecraft mailing list