[Elecraft] KPA500 transformer taps
Jim Brown
jim at audiosystemsgroup.com
Thu Jun 1 13:21:13 EDT 2017
On Thu,6/1/2017 9:41 AM, Phil Kane wrote:
> As Josh said earlier, be very concerned about the10 volt drop in the AC
> voltage measured at the load.
All great advice. Also, try to trace the wiring that feeds the outlet
that the amp is plugged into. Possible causes of the high voltage drop
are 1) conductors that are too small (AWG #14 is the smallest permitted
for a 15A circuit, #12 for a 20A circuit); 2) bad splices; 3) miswiring
of outlets or splices (reversals of hot and neutral, or hot and ground,
or neutral and ground); 4) degraded outlets; 5) miswiring of the KPA500
power cable (like #3).
For a circuit carrying this much current from an electronic load, wiring
should be a direct run of #12 (hot, neutral, and ground) from the power
panel to the outlet. While #12 is not legally required for a 15A
circuit, the larger conductors reduce IR drop.
AND -- load current to electronic loads is NOT a sine wave, but instead
consists of pulses at positive and negative peaks of the waveform to
recharge filter caps in the power supply. This causes IR drop to be
greater than predicted by application of Ohm's Law to a sine wave. SO --
it's good engineering practice to oversize conductors on circuits for
electronic loads. Two wire sizes is a good rule of thumb.
73, Jim K9YC
More information about the Elecraft
mailing list