[Elecraft] quick question about antennas

Mel Farrer farrerfolks at yahoo.com
Mon Jul 11 18:58:11 EDT 2016


The alternative on a standard duplex box is where the "blades" are at right angles to the normal outlet..  Therefore never allowing a misconnection.
Mel, K6KBE


      From: Jim Brown <jim at audiosystemsgroup.com>
 To: Reflector Elecraft <elecraft at mailman.qth.net> 
 Sent: Monday, July 11, 2016 2:21 PM
 Subject: Re: [Elecraft] quick question about antennas
   
On Mon,7/11/2016 2:07 PM, Matt Murphy wrote:
> I am guessing that installing a grounded 240V receptacle and using the 
> conduit as ground is *not* up to code. 

It depends on the building code used by local jurisdiction. In many 
jurisdictions, it IS legal to use conduit as the green wire IF it is 
continuous and all the connections are made properly. As I recall, it's 
legal in Chicago, where steel conduit is used for almost everything, in 
large part to keep union electricians working.

In other jurisdictions, or if the conduit is not properly bonded for the 
entire length, a dedicated green wire must be run.

> If it were, then perhaps I could install a NEMA 6-30 receptacle (which 
> has a ground pin and two hots). 

I don't know connectors by number, but what I would install is a 
standard outlet with two hots and ground that is slightly larger than an 
ordinary 120V outlet.  Or even two outlets in the same steel backbox, 
like a 120V duplex.

73, Jim K9YC

______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft at mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html
Message delivered to farrerfolks at yahoo.com


  


More information about the Elecraft mailing list