You are correct... it is new construction add-on to existing...
FYI, when using twisted-pair, each pair essentially functions as 4
parallel wires for cross-section... So I had to upsize to 1" RWS FMC to
accomodate 2 x 6AWG twisted pairs and not violate the 40% fill limit.
Conduit is NOT required in my locale. It is being used for shielding
only... although it is UL Listed and installed per code.
______________________
Clay Autery, KY5G
MONTAC Enterprises
(318) 518-1389
On 8/11/2016 2:45 PM, Lewis Phelps wrote:
> Depends on the conduit size. Half inch conduit can only carry two #6 wires per NEC, but 3/4” conduit is OK for four #6 wires.
>
> But we weren’t talking here about pulling wire out of an existing conduit, I don’t think.. This was described as a new installation by a code-savvy op, who no doubt is using properly sized conduit..
>
> Lew N6LEW