[Elecraft] Grounding

Kenneth Talbott ktalbott at gamewood.net
Mon Sep 28 14:26:28 EDT 2015


Tried direct response but Mr. Brown doesn't accept email from just anyone.

Several years ago the NEC relaxed the requirement that safety ground and
neutral be connected at only one place.  Now you may leave the bonding screw
in place in remote panels.

Ken - ke4rg

-----Original Message-----
From: elecraft-bounces at mailman.qth.net
[mailto:elecraft-bounces at mailman.qth.net] On Behalf Of Jim Brown
Sent: Monday, September 28, 2015 12:37 PM
To: Reflector Elecraft
Subject: [Elecraft] Grounding

On Sun,9/27/2015 10:37 PM, Fred Townsend wrote:
>
>
>   > Often the requirements of one system will be at odds with other > 
> grounding requirements. For instance you generally want a high > 
> impedance for RFI issues and a very low impedance for lightning > 
> grounds. One system defeats the other so they really need to be 
> separate systems.

> NO, NO, NO, NO!
>
>    [Fred Townsend] Well yes maybe. How do you bond a ferrite choke? 
> Are not all chokes high impedance at their intended useful frequency? 
> I said 'system' not 'ground'.
>
> [K9YC]
>
> Huh? Chokes are used on SIGNAL lines, NOT on bonding conductors. A 
> fundamental requirement of bonding is that it be LOW IMPEDANCE, so, in 
> general, bonding conductors should not be choked. Further, lightning 
> is NOT a DC event, it is an RF event. It's an impulse, with broad 
> energy peak around 1 MHz.
>
> [Fred Townsend] Correct on all scores
> Jim I think you have tunnel vision on bonding. Jim as others suggested 
> this was really an EMI issue and I was addressing this as a system or 
> EMI issue.

The bonding methods I have outlined in my tutorial are specifically designed
to satisfy both EMI and lightning protection. Proper bonding for NEC is NOT
in conflict with noise free operation of ANY system, whether it be audio,
video, or radio.

> In this case chokes are appropriate for signal AND power cords 
> containing neutral. I don't believe anyone suggested chokes on bonding 
> conductors. However you suggested everything should be bonded and I 
> merely asked how you bond a choke.

I said that ALL GROUNDS and GROUNDED equipment must be bonded together. 
A choke is neither.

Signal cables and power cables are NOT bonding conductors.  Bonding refers
to those conductors that provide a dedicated, robust, low impedance
connection between all grounded elements of premises wiring. 
Bonding conductors are those which connect together all equipment in a
station, all earth electrodes in a premises. This includes but is not
limited to the EARTH connections for CATV, Telco, satellite dishes, mains
power. It also includes those used for antennas where they enter a premises.
In simple terms, NEC (and the laws of physics) allow as many earth
electrodes as we want, but they MUST all be bonded together.

> Also the NEC as well as other codes prohibit tying neutral and safety 
> (green wire) together.

Not quite!  NEC REQUIRES that neutral and green be bonded together at one,
and ONLY one point in every SYSTEM, and, in general, requires that the bond
be very close to the point where the system is established.  
[The word "system" here specifically refers to the wiring that distributes
power in a facility, and to equipment connected to it.]  A "system" is
established when the power enters a premises, and a bond is required there.
In most premises, that's the only system. A system is also established by a
transformer, as might be used in large buildings to run large loads, and by
equipment like a UPS. In both examples, this does NOT require a new earth
electrode, but rather a bond between neutral and green at that point.

The correct part of your statement is that NEC prohibits tying neutral and
safety (green) together any place OTHER than where the system is
established.

> Two cases I called out in my four different parts of the system. So no 
> you do not tie all grounds together.

You misunderstand the concepts. See the above.  All grounds MUST be bonded
together.

Another important distinction -- a cable shield is not "grounded," and there
is no virtue in doing so EXCEPT for lightning protection. The shield is
properly connected to the shielding enclosure at each simply to make
SHIELDING continuous, and thus make it effective. This is not a GROUND, it
is a SHIELD connection. And in an unbalanced circuit (where the shield is
the signal return), it is also signal return.

When we add a common mode choke to an antenna downlead, we are preventing
common mode current on the cable shield. We bond the antenna shield to
ground at the point of entry, and we bond that point of entry to a the
building ground, but that is to protect the premises, NOT the antenna.  That
cable shield is NOT a ground, it is a shield, and it is a signal return.
That would work with a coax feedthrough, but it would not protect a rig
connected to the antenna. To do that, we replace the feedthrough with a
Polyphaser, which shorts the center conductor to the shield in the event of
a strike.

Again, I strongly urge you and others who want to understand these concepts
to study the links on my website, previously cited. Members of the AES
Standards Committee Working Group on EMC spent YEARS in discussions that
ultimately led to the understandings I've articulated. 
The members of the WG are all engineers, most with very broad background in
everything from power systems to broadcasting to recording to live sound to
RF systems. They included engineers from the BBC, ABC-TV, sound system
consultants, equipment manufacturers, and contractors. Many are/were hams.

> Furthermore I think the whole issue of grounding is exacerbated by the 
> overuse and incorrect use of the word 'ground'.

I absolutely agree, and I've preached that for years. I wrote material on
exactly that for the ARRL Handbook, and it was rejected.

> The Brits prefer to use the word 'earth' which helps a little.

Only a little -- they use "earth" and "earthing" in the same manner that we
use "ground" and "grounding" in North America, and they talk about a
"Protective Earth Conductor" which corresponds roughly to our "green wire."
I serve on the AES Standards Committee with these folks. Good people, but
they talk just as funny as we do.

> I would prefer to bury the word 'ground' and replace it with context 
> appropriate words like 'signal common' but that isn't common practice.

It should be, and I have been doing that for years. There are, at least,
four common uses of the word "ground" to describe very different things. 
I have long preached that the words "ground" and "balun" should be erased
from all literature, because they do far more to confuse us than enlighten
us.

And this question remains. When I spend MONTHS writing a tutorial on stuff
like this, and post a link to it in response to someone who obviously needs
to study it, why is it that the person won't take the time to read what I
have taken pains to write for their benefit? 
Instead, we burden the thousand or so readers of this list with a long
response that should not be necessary.

73, Jim K9YC
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:Elecraft at mailman.qth.net

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html Message
delivered to ktalbott at gamewood.net



More information about the Elecraft mailing list