[Elecraft] Got the radio...
Don Wilhelm
w3fpr at embarqmail.com
Wed Apr 16 21:37:38 EDT 2014
David,
If you add ground rods, know that all ground rods should be tied back to
the Utility ground rod by a large conductor (#6 wire is the minimum
size). That is not only a requirement of NEC safety rules, but also a
safety consideration for your station. All driven ground rods must be
connected together unless the separation between the ground rods is 100
feet or more.
My own installation has grounds that are as much as 200 feet from the
Utility Ground rod, but there are intermediate grounds that are less
than 100 feet, so *all* are interconnected by large diameter
conductors. This is primarily a consideration for AC fault conditions,
but also part of my plan for lightning protection - perimeter wires
around each building and all grounds interconnected with #6 or greater
wire to give the charge from a lightning surge a large area to dissipate
(hopefully without damage such as punching holes through the house
foundation). All towers and masts are grounded to this system.
Your home safety demands that you tie all grounds together and tie into
the utility ground system.
73,
Don W3FPR
On 4/16/2014 9:13 PM, David Cole wrote:
> Hi Don,
>
> Thank you for that info, I have powered everything, (except for the
> amp), off a single largish UPS, that way the grounds are the same, and I
> get a few minutes to kill power of the commercial power dies...
>
> I will be adding a new ground rod to the house ground system, and
> bonding that to the station ground later this week.
>
> Thanks again for the info on grounds.
More information about the Elecraft
mailing list