[Elecraft] K3 RFI in transmitted audio
Jim Brown
jim at audiosystemsgroup.com
Mon Sep 13 12:08:57 EDT 2010
On Mon, 13 Sep 2010 09:40:00 -0400, Don Wilhelm wrote:
>If we were discussing RF, then your single point ground connected to a
>low impedance ground for RF would be correct - keep the path to RF
>Ground the same distance for each piece of equipment. will achieve
what
>is needed for lightning protection.
I disagree with that concept as well. The notion that a separate wire
is required for each piece of gear to a point that is often at a fair
distance from a closely arranged collection of gear in a typical ham
shack when that gear is already well bonded together does not make
sense. How, for example, do we insure that each wire is the same
length, follows the same or a similar path, and thus has the same
inductance?
There is NO CONFLICT between bonding all equipment chassis together by
the shortest practical path, as I've outlined, and making one or more
bonds between that equipment and the earth electrode system (ground
rods).
Indeed, both IEEE Standards on Grounding and most building codes either
recommend or require multiple paths to ground for lightning protection.
A large part of the thinking behind that is that the inductance is
reduced by having multiple wires in parallel.
As hams, we tend to think of our antennas as the only source of
lightning ingress to our homes, but that is FAR from reality. It's like
looking at the circus elephant through a tiny hole in the tent. EVERY
CONDUCTOR that enters the house, and every conductor INSIDE the house,
is a receiver for energy from lightning. That's why IEEE Standards and
nearly all building codes call for ALL non-powered metal to be bonded
together, and to one or more earth connections, and for all earth
connections to be bonded togther.
One other thought on this. In thinking about how all this fuzzy
thinking about so-called single point grounding came about, one source
of it might be equipment with a pin 1 problem. If, for example, the
bonds to the equipment are improperly made to some point OTHER THAN THE
CHASSIS, then yes, lightning current WOULD go through equipment if it
was daisy-chained. But that's not a GROUNDING problem, it's an
EQUIPMENT problem, and it's IMPROPER bonding.
The good news is that I don't recall ever seeing ANTENNA connections in
ham gear with pin 1 problems (except, perhaps, for an occasional RX
antenna). It's only the audio and control wiring, and an occasional IF
output.
73, Jim Brown K9YC
More information about the Elecraft
mailing list