The AC side should always be connected to the power supply chassis -
unless it is of the "double insulated" design where no ungrounded
metallic part can come into contact with the human body. Yes, cutting
the AC "green wire ground" is a dangerous thing indeed - the entire
chassis could rise to the AC mains voltage in the event of a fault.
The power supply negative *can* certainly be floating *if* the designer
made provisions for doing that. It requires that all the common
connections on the secondary side of the transformer are isolated from
ground. As I recall, Astrons are not built that way.
73,
Don W3FPR
David Woolley (E.L) wrote:
> Rich wrote:
>
>> I had a situation with an older (analog) power supply (that had its negative
>> side grounded to the main AC ground) that tripped the Ground Fault Circuit
>> Interrupter (GFCI) in one of the bathrooms. Eliminating the bond to ground
>>
>
> I consider this dangerous advice. If you have an ELCB tripping, you do
> not treat the problem symptomatically, by creating an unsafer system,
> you find out what the real problem is and you fix it.
>
> I can't tell what the exact wiring configuration is here, but it is very
> likely that you have created a situation where there are pieces of metal
> in reach which have low impedance paths to very different "earths".
>
>