On Tue, 19 Jan 2010 17:55:04 -0500, Don Wilhelm wrote:

>I agree too, but would like to clarify that the "bonding" should not be 
>a "helter-skelter" connection of one piece of equipment to another.
>The most effective way of accomplishing that is to connect each piece of 
>equipment in the shack to a common point (which may be optionally 
>grounded or connected to a low impedance for RF (mother earth ground is 
>only for lightning protection and personal safety, not RF grounding).
>That type of bonding connection is often referred to as a "star" 
>configuration - as opposed to a 'daisy-chain' where the connection is 
>from one piece of equipment to another.

There are really at least three different issues being addressed here. 
One of them is bonding for lightning protection and power system safety. 
The bonding that I was talking about to solve this issue is specifically 
aimed at solving what I suspect are pin 1 problems in the interconnected 
equipment. So the function of the bonding I recommended is to provide a 
low impedance path from chassis to chassis, so that RF is more likely to 
flow on the bonding conductors, chassis to chassis, than on interconnect 
cables (audio and control) into the circuit board and into the circuitry 
(by the pin 1 problem). That's also the reason for ferrite chokes on the 
interconnect cables. 

I certainly agree that a very low impedance bond of all equipment to a 
single point is a good idea. BUT -- I don't want the path from computer 
chassis to rig chassis to be any longer than necessary -- I don't want it 
to go to the center of the star and back, for example. I've seen this 
"star" approach implemented with a piece of copper pipe that runs along 
the back of a radio bench, with a dozen or so wires connected at points 
that are 6-10 ft apart. By contrast, my laptop sits on my operating bench 
between two K3s, and there's a short piece of #10 braid going to both 
rigs. The third reason for bonding is to minimize the audio voltage from 
chassis to chassis that is caused by leakage current in the power system, 
and that gets added to signal for any unbalanced connection between 
equipment. By bonding that equipment with big copper, we minimize that 
voltage (and divert the current away from pin 1 problems as well). 

As for my lightning protection bonding -- THAT'S where I implement the 
star. The rigs are bonded to the power outlet green wires with a short 
piece of braid (outlets are just below the bench). The power outlets are 
bonded to the coax entry panel, also just below the bench, which in turn 
goes to a half dozen ground rods. There's also a lot of coax routed 
through various switches to the coax entry panel (with feedthrough 
arrestors). That provides a DC bond, but those coaxes have a lot more 
inductance compared to the short braids. The power outlets run in EMT 
(thinwall steel conduit) back to the power panel, which has three ground 
rods of its own, on the other side of the small building that houses my 
shack, and some #4 copper runs around the perimeter of the shack to tie 
the ground rods together that way. 

Does this clarification allay your concerns?

73,

Jim K9YC