In a message dated 7/15/07 2:13:21 PM Eastern Daylight Time, AJSOENKE at aol.com 
writes:


> The numbers look kind of  low don't they? These are for DC continuous  duty 
> 
> cycle. 

The same is true for house wiring. 

> run 6 or 8 GA in my mobiles ( also using silver plated with many more 
> strands 
> than the hardware store variety ). 

The real issue is voltage drop, particularly in a 12 volt system where you 
may not have a lot of spare volts to play with. I don't think #6 or #8, or their 
paralleled equivalents, are overkill in such applications.

We just installed #8 on a 240 line in the 
> 
> house for AC that mfg specified as a 40 amp circuit - way more than the AC  
> uses.
> 

#8 is the standard house-wiring size for 40 amps - #10 is only good for 30 
amps. And while the AC may not draw 40 A continuous, the initial starting surge 
may get up there. Don't want nuisance trips! 

> I don't spec my DC operating Cables on basis of maximum current carrying  
> capability, but rather for best DC resistance characteristics. 

That's the way, regardless of short or long runs.

73 de Jim, N2EY




**************************************