Something important to keep in mind (which I'm sure Steve has done but
didn't mention) is that in addition to the antenna leads which go
through the lightning suppressors at the entrance plate to the house,
you should also pass ALL of the AC, telephone, rotor, etc. lines for the
shack through the entrance plate with appropriate suppressors. That way
there shouldn't be any large differences in potential between circuits
inside the shack if there us a nearby strike.
I have a sort of Mickey Mouse version of Steve's setup: several ground
rods at the base of the tower with the outsides of the coax lines
grounded there, a single entry plate (mine is aluminum) with suppressors
mounted on it and a couple of ground rods near that. All of my ground
rods are connected together with a no. 4 solid copper conductor buried
under the ground (which also goes to the ground rod at the AC line
entrance). I use the ICE brand of suppressors for the coax lines and
the rotor wires, as well as a whole-house type of surge protector for
the AC line. All this stuff is mounted on the entry plate which is in a
box on the outside of the house, and the plate is connected to the
ground rods with a 2" wide copper strap.
I keep the only telephone in my ham shack about 4' from the equipment
and the telephone line is not connected to the shack computer at all.
If you need a phone on your operating table or have a modem in your
shack computer, then the phone line should also come through the entry
plate with a lightning suppression device.
My setup could be improved in many ways: the no. 4 conductor and ground
straps from the entrance plate are only clamped, not bonded; the no. 4
conductor should be buried deeper (mine is just a few inches below the
surface), there should be more ground rods further from the house, the
tower should be away from the house and not bracketed to it (!), and so
forth.
Best regards,
Vic Rosenthal