When the neutral failed, the sides of the flat two-phase were unbalanced.
Instead of it being 120-0-120; the voltages were divided unequally, such
as 210-0-30.
The line-to-line stayed the same, but the line-to-neutral went way up on
one side, way down on the other.
The overvoltage blew stuff.
-John
===================
> All,
>
> Maybe you can help me understand some damage to the electronics of my
> neighbors.
>
> During the recent northeast snow storm ten neighbors, all on one PPL
> transformer, lost power. Power was lost because branches pulled the
> electric services from both halves of a duplex (semi-detached house).
> At the same time that the power was lost, there was a voltage spike that
> blew out all kinds of solid state devices (Yeah, I know, if they had
> tubes...). What were lost were things that are always on (stoves,
> furnaces, heat pumps, microwaves) or "on" even when they are turned
> "off" (TVs, principally). There were reports that the lights suddenly
> became brighter and that there was a sizzling noise.
>
> The story is that, when the two services were pulled from the walls, the
> neutrals were broken and the spikes were the result.
>
> Would someone please explain why the voltage spiked when the neutrals
> were lost?
>
> Thanks,
>
> Ron
>
> --
> Ron Hunsicker
> 1238 Cleveland Avenue
> Wyomissing, PA 19610-2102
> 610-478-0371
> ronhunsi at ptd.net
>
> ______________________________________________________________
> Boatanchors mailing list
> Home: http://mailman.qth.net/mailman/listinfo/boatanchors
> Help: http://mailman.qth.net/mmfaq.htm
> Post: mailto:Boatanchors at mailman.qth.net
>
> List Administrator: Duane Fischer, W8DBF
> ** For Assistance: dfischer at usol.com **
>
>
> This list hosted by: http://www.qsl.net
> Please help support this email list: http://www.qsl.net/donate.html
>
>
More information about the Boatanchors
mailing list