Ron Freeman, K5MM, asked about getting 100 uf, 500 volt
electrolytic capacitors.
A few companies such as Nichicon and Vishay (both Asian),
and Cornell-Dubilier still make 500 volt electrolytics but
these are extremely difficult to find. Most manufacturers
make electrolytics with working voltage ratings no higher
than 450 volts.
The problem is that it is extremely difficult to make such
capacitors. To form the anodic aluminum oxide film on a
typical 450 volt electrolytic, a forming voltage in excess
of 600 volts may be used. The anodic film formed, the
actual dielectric of the capacitor, will be about 900
nanometers thick (about 35 millionths of an inch for those
thinking in English units). This is less than one
hundredth of the thickness of a human hair.
At voltages above 600 to 700 volts, scintillation effects
occur in the anodic film. This is where microsparks occur
at surface irregularities. Unless the current is very
limited, this leads to rapid puncture of the insulating
film and a shorted capacitor. With great care, 500 volt
electrolytics can be built, but most manufacturers settle
for 450 volts as a safe upper limit. [Similarly, tantalum
electrolytics have a practical upper voltage of around 50
volts with 35 volt units being the highest voltage units
commonly available.]
You may occasionally find older electrolytic capacitors
with ratings up to 800 volts. But if you open these up,
you will find they are just two lower voltage units in
series.
This should give you a hint on how to get the capacitance
you need. Just use two lower voltage, higher
capacitance units in series. If you use randomly picked
electrolytics, I would go with two 300 volt units in
series, but if you purchase new units from the same
manufacturer, two 250 volt units should suffice. The reason
for applying a larger safety factor with different units is
due to variations in leakage current.
Balancing resistors, to equalize the voltage across the two
capacitors, are a good idea. Typically you would size the
balancing resistors to draw at least 10 times the
capacitor's rated leakage current. Remember that resistors
have a maximum voltage rating too. Most resistors made
today in the 1/2 watt size are rated to only 250 volts (and
sometimes 350 volts). This is independent of the power
rating of the resistor.
73, Dr. Barry L. Ornitz WA4VZQ [email protected]