[AMRadio] AMRadio Digest, Vol 90, Issue 22
D. Chester
k4kyv at charter.net
Wed Jul 27 11:23:20 EDT 2011
>> Electric kitchen ranges with 3-wire plug run on 240V, with the neutral
>> and
>> ground bonded together. So does the BC1-T broadcast transmitter in
>> original configuration.
> And, so does the Alpha 70 and 77 series of HF amps -- along with some of
> the
> big Henry models. In the case of each amp, neutral is used to run a
> 120VAC
> blower. In the Alpha 70/77 they made it easy to separate neutral from
> chassis ground by cutting a jumper on the Cinch-Jones power plug. The
> change doesn't even occur inside the amp. I ran 4-wire, #8 AWG between
> the
> panel and the shack, terminating into a 30-amp twist-lock receptacle. My
> only dilemma is that I have one receptacle and four amps, requiring a
> physical change of the power plug when changing between amps. No really
> good solution comes to mind, mostly for convenience reasons.
>
> At the time these devices were manufactured, it was acceptable to join the
> chassis to the neutral connection. 40+ years ago, the NEC may have
> strictly
> forbidden this practice, but the NEC is a premise wiring standard -- not a
> products wiring standard. So, perhaps the root of this really goes back
> to
> what was allowed under UL guidelines at the time. Well after 1970, the
> manufacturers seem to have gotten the idea and had found a means to better
> utilize the blower between 120VAC and 240VAC service.
>
> Paul, W9AC
Strapping neutral to ground at any point beyond the entrance panel is not
only a safety hazard; it can wreak havoc with certain equipment by causing
ground loops. Ideally, if I could find them, I would use heavy duty 240
to120v isolation transformers, each with a mid-tapped 120v secondary, to run
all the 120v stuff in the house. Of course, that would run up the power bill
slightly because transformers are not 100% efficient and each one would have
a little power loss. With balanced 120v lines, the biggest jolt you could
get from hot to ground would be 60 volts, and the balanced line would take
care of most of the ground loop problems. I understand the navy uses
balanced 120 volts on shipboard just for that - safety reasons.
A lot of our ground loop and ground fault problems would not exist if the
mains voltage were universally 240v to run everything, and the mid-tap on
the pole pig secondary were strictly a safety ground and we never tried to
pull any current through it. Every appliance would have a 3-prong plug: two
hots and a ground. That's the way they do it in many countries round the
world with no problem. It would also save energy by reducing the voltage sag
in wiring. I suspect our 120/240 system was already too well established to
change before all the problems became apparent, so the best we could do was
to add the requirement for separate ground and neutral. Old 220v
receptacles had nothing but two "hot" prongs, but they lined up differently
from the ones on110v plugs so the wrong appliance couldn't be plugged in to
the wrong voltage.
This house was first wired in the 1930s, and none of the original wiring
even has a ground conductor. All the original outlets are two-prong only.
Unfortunately, they didn't use knob-and-tube wiring, but what was at that
time supposed to be the latest and greatest: that old style romex-like stuff
with rubber insulation covered with tar-impregnated cloth. The dried-out
insulation on the old wiring is very fragile and brittle, but it would
require ripping through walls and ripping up floor boards to replace it, so
I have always been content to just be careful with it. Every connection was
soldered, which I think is better than those flaky wire nuts that can cause
a fire if they are not assembled and tightened properly, and leave a loose
connection that eventually begins to arc. Knob-and-tube, if installed
properly and not tampered with, should never fail even if the insulation
dries up and falls completely off the wire.
Paul, why couldn't you just wire in three more receptacles so you would
have a separate one to accommodate each of your amps, and not have to do all
that plugging and unplugging nonsense? You could even make it work like a
power strip, with one heavy duty plug connected to the main receptacle, and
a cable feeding four additional surface-mount receptacles mounted side by
side on a board or metal panel.
Don k4kyv
_______________________________________________________________
This message was typed using the DVORAK keyboard layout.
http://www.mwbrooks.com/dvorak/
http://gigliwood.com/abcd/
More information about the AMRadio
mailing list