[AMRadio] UTC CG-305

Donald Chester k4kyv at hotmail.com
Sat Sep 28 14:23:56 EDT 2002



>From: Charles Ring W3NU <charlesr at infonline.net>
>
> > Someone else said that the output was
> >
> > High voltage 2400-1750-0-1750-2400VAC, DC voltage 2000/1500, 300 mA 
>continuous
> >
> > yet the critter is labled (engraved, even) 3500 and 4800.  That's 
>-gotta- be
> > across
> > the entire secondaries...

>...it's the same rating, with the center tap as the zero reference.
>The DC voltage is based on a full wave rectifier using the center tap.


Be careful when using such a transformer in a full wave bridge ciccuit.  
Sometimes transformers designed for full wave CT operation do not have HV 
insulation at the CT, since it is assumed by the manufacturer to be at 
ground potential.  Running it in a FWB could result in a zorch to ground at 
the CT of the winding.

The same precaution is recommended when placing the filter choke between CT 
and ground instead of the more traditional positive side of the filter.  The 
high ripple voltage that appears across the choke will also appear at the 
transformer CT and could cause failure of the transformer.

I'll look up those ratings in my UTC catalogue this evening and verify.

Don K4KYV